[Radiance-general] illuminance on external facade

Stephen Selkowitz seselkowitz at lbl.gov
Thu Mar 28 00:13:04 PDT 2013


Rob and others
The very high numbers (>300) are not physically plausible (at least on this
planet with its atmosphere and sun). You can get numbers in the 200l/w
range if you filter sunlight through spectrally selective glass.  If I had
to guess, without doing any homework, its an artifact of the derivation as
follows: I assume diffuse radiation is calculated by processing measured
global irradiance and measured or assumed beam, and that diffuse
illuminance is calculated by processing measured global illuminance and
measured or assumed beam, so you are comparing two "small" numbers, each
the result of subtraction of two much larger numbers, so that relatively
small errors in the original calcs are magnified by that derivation.  If
someone has time to dig into the source data you could verify or expose
another source.  Of course it could be direct measurement and just a batch
of poorly measured/calibrated/reported  data.

Steve

**********************************************************************

Stephen Selkowitz

Building Technology and Urban Systems Department             (510) 486-5064

Bldg.90-3111
       fax (510) 486-4089

Lawrence Berkeley National Laboratory
SESelkowitz at lbl.gov

Berkeley, CA 94720
http://buildings.lbl.gov/ <http://BTECH.lbl.gov/>

**********************************************************************


On Wed, Mar 27, 2013 at 8:51 AM, Guglielmetti, Robert <
Robert.Guglielmetti at nrel.gov> wrote:

> **
> Hi John,
>
> Thanks for looking at this. This is indeed interesting. When I get back in
> the office I can at least ask around if the measured versus derived
> illuminance question is answered somewhere in the weather file. As to the
> reason(s) why the efficacy for diffuse horizontal flaps around, I'm
> stumped, and unclear if its cause for alarm. Anyone?
>
> Rob
>
>
>
> Rob Guglielmetti
> NREL Commercial Buildings Research Group
> Golden, CO 80401
> robert.guglielmetti at nrel.gov
>
>
> -----Original Message-----
> *From: *John Mardaljevic [j.mardaljevic at lboro.ac.uk]
> *Sent: *Monday, March 25, 2013 03:44 PM Mountain Standard Time
> *To: *radiance-general at radiance-online.org
> *Subject: *Re: [Radiance-general] illuminance on external facade
>
> Hi Ery,
>
> Tinkering with the Boise TMY3 data I was a little surprised to see how
> some of the efficacy values turned out.  For those unfamiliar, the Boise
> TMY3 climate file (much like many of the others from the Energy+ website)
> contains both illuminance and irradiance data for these quantities:
>
> - Global horizontal (Gh)
> - Diffuse horizontal (Dh)
> - Direct normal (Dn)
>
> Sometimes illuminance data is derived from irradiance measurements, though
> nowadays it is more likely to be measured separately.  Which it is could be
> identified in the climate file (I haven't checked).
>
> The following table shows how the mean luminous efficacy (within 5klux
> bands of global horizontal illuminance) varies for: the global horizontal;
> the diffuse horizontal; and, the direct normal quantities:
>
> gh_lo           gh_hi      Eff_gh          Eff_dh          Eff_dn
>
>        5000.00      10000.0      106.145      135.606      60.1583
>       10000.0      15000.0      106.610      147.202      73.0784
>       15000.0      20000.0      107.339      258.167      81.6775
>       20000.0      25000.0      108.312      140.848      88.2379
>       25000.0      30000.0      107.261      156.417      92.4818
>       30000.0      35000.0      106.713      184.455      94.1426
>       35000.0      40000.0      106.456      197.996      96.1488
>       40000.0      45000.0      106.142      213.014      97.9623
>       45000.0      50000.0      105.894      177.705      99.2376
>       50000.0      55000.0      105.992      173.584      100.170
>       55000.0      60000.0      105.812      179.285      100.867
>       60000.0      65000.0      106.057      300.989      101.701
>       65000.0      70000.0      105.593      129.234      101.205
>       70000.0      75000.0      105.347      145.367      101.420
>       75000.0      80000.0      105.333      193.799      101.418
>       80000.0      85000.0      105.044      135.980      101.445
>       85000.0      90000.0      104.697      134.219      100.965
>       90000.0      95000.0      103.924      123.413      100.588
>
> The global efficacy value (Eff_gh), as you noted, is between 100 and 100
> lm/W -- I'd expect global vertical to be very similar to global horizontal,
> at least for sun illuminated orientations.  Direct normal efficacy across
> the ranges is also pretty much how I expected it to vary.  However, diffuse
> horizontal efficacy seems to flap-around quite a bit -- four maxima, two of
> them quite conspicuous.  I wouldn't have been too surprised to see general
> trends, but this was unexpected.  Can't say that I've noticed or given much
> thought to it before, but I am a little intrigued by those high values,
> i.e. > 200 lm/W.
>
> Best
> John
>
>    John Mardaljevic
> Professor of Building Daylight Modelling
> School of Civil & Building Engineering
> Loughborough University
> Loughborough
> Leicestershire
> LE11 3TU, UK
>
> Tel: +44 1509 222630 (Direct)
> Tel: +44 1509 228529 (Pam Allen, secretary)
>
> j.mardaljevic at lboro.ac.uk
> http://www.lboro.ac.uk/departments/cv/staff/profile/367.html<http://www.lboro.ac.uk/departments/cv/>
>
> Personal daylighting website:
> http://climate-based-daylighting.com
>
>
> _______________________________________________
> Radiance-general mailing list
> Radiance-general at radiance-online.org
> http://www.radiance-online.org/mailman/listinfo/radiance-general
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://www.radiance-online.org/pipermail/radiance-general/attachments/20130328/62a59bc2/attachment.html>


More information about the Radiance-general mailing list